Hi Theasteroidbelt,
Should you want good safety and not the expense of the-wiring the building, consider installing ground fault interrupter receptacle outlets or ground fault circuit interrupter circuit breakers at the earliest point you can in the circuit. This will protect all downstream devices and the boxes to which they are bonded.
Why?
The grounding terminal on "modern" switches is attached to the yoke by which you mount the device. This can present a hazard:
If the device box isn't grounded and there is no equipment grounding conductor; a "modern" switch with a grounded yoke that experiences a failure (or an energized conductor touches it) it can energize the device box, the face plate and the screws. I work only very little residential (friend & family freebies), but twice in the last year I've encountered found this problem at houses. Both people called me because they touched a switch plate and got shocked.
If the device box into which they will be mounted in is well grounded, then there are no worries about using new switches without an equipment grounding conductor in the box.
Paul