Jude_electricals
New member
- Joined
- May 17, 2025
- Messages
- 4
Got called to a job where someone installed a 95mm 3 core SWA from the meter to a workshop about 120m away, then branched off to the main house and garage using 16mm tails. They're relying on the SWA armour as the main earth, but the terminations are sloppy and the ZE reads 0.75. The armour's cross section is too small for proper earthing at that length I figured a 50mm SWA would've been the right size but the customer refuses to upgrade the cable, so I'm stuck deciding whether to fix the terminations and see if the earth reading passes or recommend switching the buildings to TT systems. What's your take?