I’m installing a subpanel in an attached garage/shed and want to use an outdoor rated (NEMA 3R) panel I already have on hand
it feels like a win-win because it’s a dusty woodshop environment, the space is unheated, and the wall has had leaks in the past
I'm planning to run Teck90 with weather tight connectors to keep it all sealed up.
is there anything in the Electrical Code that stops me from using an outdoor rated box inside a building?
Seems like the extra protection against dust and moisture is a plus, but I want to make sure an inspector won't flag it for being over spec
Any CEC experts have thoughts on this?