Hi DarkHector,
BarryEnergy made a very good point about AFCI.
You mentioned shared netural. Did you run 2 new circuits with a shared neutral?
Some AFCI have trouble with shared neutral & separate breakers. If I remember correctly, Eaton BR is one brand that has problems. If you have a shared neutral, most manufacturers want a two-pole AFCI for those circuits.
Note, too, that combination arc fault-ground fault circuit breakers cause lots of problems with shared neutrals. Using 14-2-2 or 12-2-2 NM cable would be the best plan for two AFCI-GFCI circuits scenario. (One cable run for two circuits)
Unfortunately, AFCI problems can be tedious to troubleshoot. Since you already know that the connections are done properly, it would be wise to remove one item at a time in order to find out who is the troublemaker.
Example:
Recently, I was called for AFCI tripping randomly. What I found was a wall sconce that had a partially separated conductor within the fixture itself. Even with the lamp off, the AFCI would occasionally trip when anything else was connected to the circuit. Once the lamp was removed from the circuit, all was good. (Taking the fixture apart confirmed the partial separation in the conductor.)
Keep in mind that some devices trip AFCI even when working properly. We had a bread toaster that would trip AFCI. The little arc when the lever was pushed down was too much for the AFCI, so it tripped. Things with contactors and relays also sometimes can trip AFCI- even though they are working properly. Items with no switch or a switch turned on when plugged in can also trip AFCI due to the load. Items with heating elements are prime candidates.
Another strong possibility is simply a defective circuit breaker (AFCI or non-AFCI). Even a brand new circuit breaker can randomly trip with a light load or even with no load if it is defective, Do you have another circuit breaker to swap in for a check out?
Some brands have a higher defect count than others. Square D Homeline is an example of a brand with high defect count.
Hope This Helps!