ran into a crazy service call today. the customer smelled that an electrical burn just a week after their 48amp Wallbox install.
I showed up and find the 60A breaker completely melted, but still powered on!
everything looked perfect on paper. I checked the Polaris taps, the energy management module, and all the connections
everything was torqued to spec with no signs of arcing
then I bypassed the module and installed a brand new breaker to rule out a fluke. we verified 48 amps on each leg with perfect voltage at the car and the panel. within minutes, the burning smell was back and the new breaker started overheating immediately.
my manager and engineer are confused. we're replacing the whole panel for free to be safe, but I’ve never seen a setup bypass all the math and just cook like this.
has anyone else dealt with a panel busbar failing under a steady EV load, even when the connections are tight? what are we missing?